    Lightbulb Infraspection Tip of The Month - Measuring motor temperature

    Measuring motor temperature is often a challenge since electric motors differ in their design and construction. While many have suggested measuring the motor casing along the stator, this method does not work well for motors that are fan cooled or exposed to external air currents. For uncooled motors, this approach can produce varying temperature values depending upon the location of the subject temperature readings.

    In 1997, a research project led by Infraspection Institute utilized instrumented motors in a controlled environment to determine the effect of excess force on installed motors. One of the primary goals of this research was to identify a location for collecting reliable temperature data.From our research it was found that measuring the exterior of the motor bell housing within 1” of the output drive shaft consistently produced temperatures that were within 1 to 2 Celsius degrees of the motor windings and the inboard bearing assembly.Temperatures taken at the bell housing were especially useful for fan-cooled motors since this area was unaffected by convective cooling from the fan.When measuring motor temperatures, keep the following in mind:Make certain that all thermometers are within calibration and used properly Motor temperature will vary with load and ambient temperature.
    Admin is a forum identity we (CITA) use to post on behalf of others & also for official forum posts.

  2. #2
    So even though there is some distance and cooler regions between the area near the output shaft (to take the Temp measurement) and the windings suspended inside the body of the motor case, the bearing and those windings were found to be at a similar temp.
    Excellent tip.